520.1 talks to auditoriums in schools. Does this mean that the classrooms can be wired in romex but the rooms that hold over 100 people need MC :? Lets say it's a class of structure that will allow NM.
 
Last edited:

iwire

Moderator
Staff member
Location
Massachusetts
520.1 talks to auditoriums in schools. Does this mean that the classrooms can be wired in romex but the rooms that hold over 100 people need MC :? Lets say it's a class of structure that will allow NM.

It is possible depending on the construction methods.
 

kwired

Electron manager
Location
NE Nebraska
520.1 talks to auditoriums in schools. Does this mean that the classrooms can be wired in romex but the rooms that hold over 100 people need MC :? Lets say it's a class of structure that will allow NM.

Are you talking about a 518 or 520 installation? 518.1 pretty much says that it applies except for places explicitly covered by 520.1. I take that to mean anything in 518 applies unless 520 adds to or takes away from what is mentioned in 518.

I think the answer to your question is in 518.2(B). Around here the AHJ will want to see at least 1 hour rating between separate areas before considering them separate areas.
 