First post for me so be gentle. I have been a licensed electrician for 20 yrs and have just decided to get my Masters, don't ask why:happysad: Anyway I am taking a correspondence course at home for the 45 hour requirement and am having brain cramps about figuring out grounded conductor, main bonding jumper, grounding electrode conductor sizing. Below is an example of a question in the book.
Determine the minimum size Cu grounded conductor required for a 120/208 V 3 phase 4-wire service which consists of two parallel 1/0 AWG THW Cu conductors per phase.
Now I have looked over 250.66 and 250.24 c (1) and chapter 9 table 8
A couple of things confuse me one being the question stating (2) parallel 1/0 conductors, and the other being in chapter 9 table 8 where the wire size is in mils.
I know if I had if I had 3 phase 4-wire 480/277 service with three 500 Kcmil Cu THW conductors per phase
per 250.66 500x3= 1500 Kcmil
per 250.24 1500Kcmilx12.5% = 187500 cm
Ch 9 table 8 187500cm=4/0 AWG THW Cu
Determine the minimum size Cu grounded conductor required for a 120/208 V 3 phase 4-wire service which consists of two parallel 1/0 AWG THW Cu conductors per phase.
Now I have looked over 250.66 and 250.24 c (1) and chapter 9 table 8
A couple of things confuse me one being the question stating (2) parallel 1/0 conductors, and the other being in chapter 9 table 8 where the wire size is in mils.
I know if I had if I had 3 phase 4-wire 480/277 service with three 500 Kcmil Cu THW conductors per phase
per 250.66 500x3= 1500 Kcmil
per 250.24 1500Kcmilx12.5% = 187500 cm
Ch 9 table 8 187500cm=4/0 AWG THW Cu