20 amp breaker on 30 amp wire

Status
Not open for further replies.

Part-Time

Member
Location
Houston, Texas
Can you put a 20 amp double pole breaker on
A 30 amp (#10) wire or would the breaker have to be sized to
Wire and use a 30 amp DP breaker. The load on the window AC
is 16 amp max it heats and cools. Any code reference that would help?
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
The breaker is the protection for the wire, generally speaking. Many times we increase the wire size for VD but the breaker still must be sized to the circuit it protects.
 

kwired

Electron manager
Location
NE Nebraska
Can you put a 20 amp double pole breaker on
A 30 amp (#10) wire or would the breaker have to be sized to
Wire and use a 30 amp DP breaker. The load on the window AC
is 16 amp max it heats and cools. Any code reference that would help?


Put 500 KCMIL onthe 20 amp breaker if you want. You will need some kind of adapter to make it fit however.
 