Barndog
- Spring Creek Pa
Why in motor controls do they run the overloads through the neutral (L2) side but all other switches are on the L1 side??
L1 is where you typically land the black or hot conductor on a 120 volt starter. L2 is the neutral. You want the hot as the front end of your control circuit and not the neutral.
It is much easier to wire a multi-coil assembly (i.e. reversing starter) if the OL relay contact is on the L2 side.
Both of which present the possibility of field wiring affecting the relatively 'unrobust' overload contact (which normally has poor short circuit withstand ability), whereas its factory location renders it relatively safe from wiring misuse/abuse.you could run L2 through the overload relay then pigtail to both coils but you could also do with L1 if you put the OL first then parallel the other contacts to the two contactors.
I am not saying "L2" is the best location, I am simply providing historical reason why NEMA and JIC standards have allowed it to exist where it does.