I have a DC conduit run in EMT going from a photovoltaic array to the inverter. The conduit run contains a positive, negative, and an insulated (not bare) EGC (not a GEC).
The conduit run starts with a ground bushing on the roof and ends with a ground bushing at the inverter. But there is a pull box in between. The conduits that enter and exit the pull box just have plastic pull bushings but I put a ground bar in the pull box through which the EGC lands (unbroken) before it continues on.
My question is does this suffice? Or do I absolutely need ground bushings or myers hubs entering and exiting the pull box?
Thanks in advance.
The conduit run starts with a ground bushing on the roof and ends with a ground bushing at the inverter. But there is a pull box in between. The conduits that enter and exit the pull box just have plastic pull bushings but I put a ground bar in the pull box through which the EGC lands (unbroken) before it continues on.