Bonding underground conduits

Status
Not open for further replies.

Brandon Loyd

Senior Member
If metal conduit from underground feeds a metal enclosure, is it required for all metal conduits coming from underground be bonded to the metal enclosure?
 

Attachments

  • DSCN0159.JPG
    DSCN0159.JPG
    43.4 KB · Views: 0

Brandon Loyd

Senior Member
Are you sure these code sections apply? It looks like these code sections are for armored cable. If the conduits are suppose to be bonded to the EGC, which doesn't exist, wouldn't the underground metal conduits be acting as the EGC and thus need to be bonded together and to the metal enclosure?
 

raider1

Senior Member
Staff member
Location
Logan, Utah
Are you sure these code sections apply? It looks like these code sections are for armored cable. If the conduits are suppose to be bonded to the EGC, which doesn't exist, wouldn't the underground metal conduits be acting as the EGC and thus need to be bonded together and to the metal enclosure?

Yes, 250.86 would apply to non-service raceways.

Chris
 