non-ul listed fixtures

Status
Not open for further replies.

raider1

Senior Member
Staff member
Location
Logan, Utah
To add to what Bob posted 410.6 requires all luminaries to be listed.

Also keep in mind that there are other listing agencies other than just UL, such as ETL CSA etc...

Chris
 

raider1

Senior Member
Staff member
Location
Logan, Utah
For all fixtures yes, fixtures for wet locations, hazardous locations etc. where already required to be listed. (I believe)

Correct, 410.4(D) required luminaires located in bathtub and shower areas to be listed for damp locations or wet location where subject to shower spray.

Chris
 
Status
Not open for further replies.
Top