225.30(E) Multiple Feeders to a building

Status
Not open for further replies.

retire09

Senior Member
If a building is determined to qualify for 225.30(E) for having documented switching procedures; will each feeder still require
a service rated disconnect,
connected to a grounding electrode system
all building disconnects be grouped in one location
not exceed 6 switches?
I have a plan showing several feeders from another building supplying different panels thruoghout the building.
225.30(E) only exemps the installation from the one set of feeders.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Art. 225.33 states that the disconnect means for each supply permitted by 225.30 shall consist of not more than 6 disconnects. Does that answer the question
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
In my opinion, (E) simply allows you to have more than one feeder if you meet the requirements, but each must still comply with all other requirements.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
In my opinion, (E) simply allows you to have more than one feeder if you meet the requirements, but each must still comply with all other requirements.

I agree with Gus. Grounding electrodes all the way around and service rated disconnects.
 