Look at 250.66 and remember the gec never needs to be larger than #6.
The title of the thread is ground rods....I thought that was what we were talking about. And yes if you use the rod as a bonding jumper to a water pipe or another electrode than it may need to be larger than #6. I'll say almost never....and I have never used an electrode larger than #6 to the thousands of rods I installed.Never say never. The #6 max rule only applies to rod plate and pipe electrodes.
I always use #6 for every service between 100-400 amps. Never done one bigger or smaller, so I don't know what I would do in either of those situations.
We just use #6 Cu for every size service to the rods.