Disconnect Question
bodineb50
oregon
I recently ran a 20 amp multiwire branch circuit out to a detached garage and used a nonfused 30 amp rated disconnect.
The inspector failed the installation citing 225.36 and said that it needed to be service entrance rated, my thoughts are if the exception to that article allowed me to use a 2 pole switch as a disconnect to disconnect the mwbc then surely a disconnect with heavy copper blades would be ok.
I ended up taking out the disconnect and installing a switch to pass inspection but was thinking that it didnt make sense, has anyone else come across this kind of thing?
Although I agree with your logic a cheap snap switch is all that complies with the exception.
225.36 Suitable for Service Equipment.
The disconnecting means specified in 225.31 shall be suitable for use as service equipment.
Exception: For garages and outbuildings on residential property, a snap switch or a set of 3-way or 4-way snap switches shall be permitted as the disconnecting means.
Here is the rule:
225.36 Suitable for Service Equipment. The disconnecting
service equipment.
Suitable for use a service equipment means there is a neutral bus with a removable main bonding jumper. Your unfused switch may of been suitable for use - it would be right on the label if it was. If it was fused, it would of been listed as suitable...
I agree with the others however I think that is BS for an inspector to turn that down. An a/c disconnect, although not service rated is no worse than a snap switch. In fact I think the disco is better than the snap switch--- I think common sense needs to be used here.
Well common sense says one thing but the NEC words as written don't support yours, mine or bodine's opinion.
Yep so here is my proposal
225.36 Suitable for Service Equipment. The disconnecting means specified in 225.31 shall be suitable for use as service equipment.
Exception: For garages and outbuildings on residential property, a snap switch, or a set of 3-way or 4-way snap switches, or other approved non service rated disconnect shall be permitted as the disconnecting means.
Here is my substantiation
As this section is written I can run a multiwire branch circuit to a dwelling garage and use a DP snap switch as a disconnect but I can be rejected for using a non-fused disconnect such as an a/c pullout style disconnect. These a/c disconnects are not usually service rated. Why would a disconnect need to be service rated if one can use a snap switch? This proposal will help clarify what I believe to be the intent of this section. I realize this may seem petty but I know of a few people who have been rejected for this install.
I think the suitable for use as service entrance requirement needs to be removed. A device rated for use as service entrance equipment either has a factory installed main bonding jumper or a field installable main bonding jumper. Since feeders to remote building are required to include an EGC now there is never a reason to bond the neutral in the service disconnect.
I believe the "service rating" is required for when there is a presence of an operating load through the equipment during the "off/on" operation of the disconnect.
I would approve a 30 amp non-service rated switch, for a residential property.
Thanks alot for the replys, usually when we get "dinged" for something petty I just
make the correction and move on.
This time I felt the inspector should have exercised common sense and thought about what the intent of the code is for this situation and allowed it for it meeting the intent.
Dennis, I liked the proposal and the substantiation and it seems like it makes perfect sense.
Thanks again for the replys.
I really don't understand why a 3 or 4 way snap switch is allowed to be used as a disconnect. Shouldn't there be an off/on indication?
I think it would be BS if the inspector did not do the job he is required too.
It was used here, the inspector new the code and commonsense says the inspector has to enforce the code.
Now if someone gets this section changed ......... :)
another one of those issues where the code is not appilied with consistency and common sense.