beanland
Senior Member
- Location
- Vancouver, WA
I want to run a 200A 3-wire cicuit using aluminum conductor. 4/0 THHN AL is rated 205A @ 90C. So that works for the conduit. 
But, I must land on the terminations at 75C. 4/0 THHN is rated 280A @ 75C in free air at the terminations. Since I am only loading it to 200A, I am good.
Right or wrong?
	
		
			
		
		
	
				