Timtrewyn
Member
- Location
- Fort Pierce, FL
I am working with an existing industrial installation that has been operating with a feeder using two sets of #2 CU, each set installed in 1 1/4" EMT under emergency conditions.  The load is less than 60 Amps and is not going to grow.  That was not known at the time of installation.  I am aware the 2002 Handbook says "there does not appear to be any practical need to parallel conductors smaller than 1/0 AWG."  The AHJ is now catching up with inspecting these emergency installations and is citing a violation of 310.4(A).  What is the hazard?
	
		
			
		
		
	
				
			 
				
 
 
		 
 
		 
 
		 
 
		 
 
		