Wiring 3 phase transformer

Status
Not open for further replies.

Smart $

Esteemed Member
Location
Ohio
I'm guessing that somewhere in the annuls of transformer wiring there's a note that says midpoints of three windings are an XO and midpoints of a single winding are X4.
X0 is not the midpoints of three windings. It is a common connection of one end of each of three windings, also known as a wye configuration of the windings.

X4 is used for three phase transformers to denote it is a midwinding tap of one of the three windings which are delta configured. Yet a single phase transformer with a midpoint winding tap terminal is not marked X4. Also, if you have a two-winding secondary, single phase transformer, the terminals are typically denoted as X1, X2, X3, and X4... so X4 does not exclusively denote a midwinding tap.
 

noelelectric

New member
Location
miami ,fl usa
always h.. are primary site and x... are secondary site

always h.. are primary site and x... are secondary site

X4 is typically a mid-winding tap... and definitely not the same as X0;i agree with u.
h1.h2.h3 is for 208 volts(primary is'nt low o higt volts,its just your conexion source) and x1 x4 x2 x3 are secundary site,you have two coil x1 and x2; x3 x4,thats is if you want to make paralle conexion with other trasnmformer ore series to use 480 volts,and remember on 480 volts u dont need a neutral.
 