G greg3030 Member Location seattle wa Jul 5, 2011 #1 looking for code article if a singie 20amp circuit is okay for a detached garage.
augie47 Moderator Staff member Location Tennessee Occupation State Electrical Inspector (Retired) Jul 5, 2011 #2 You may find what you need in 225.36
Dennis Alwon Moderator Staff member Location Chapel Hill, NC Occupation Retired Electrical Contractor Jul 5, 2011 #3 I would also look at 225.30 as well as most of 225 section II
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician (retired) Jul 5, 2011 #4 Generally you don't need to run any circuits to a detached garage. If you do I would run 1-3 wire MWBC. That way you would end up with two circuits and still wouldn't need a GES. One extra condcutor and twice the capacity.