Aluminum or copper service entrance conductors

Status
Not open for further replies.

arnettda

Senior Member
In a residental setting with the POCOS meter on the outside of the house and your 200 amp main breaker panel inside the house. What is your preffed conductor material and why? Say less than 12ft of conductor overall. I have been using AL. The wire comming into the meter is aluminum and it is cheaper and I am asking to find out if it is good enough. Or should I switch to CU.
Thanks
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
There is nothing wrong with properly installed aluminum conductors. They're a little less forgiving than copper however.
 

John120/240

Senior Member
Location
Olathe, Kansas
Aluminum is acceptable for service conductors. How ever we have one city that

requires copper service conductors. All it does is drive the cost of the install

higher. Anayway as long as you get paid whats the difference.
 

Cow

Senior Member
Location
Eastern Oregon
Occupation
Electrician
There are a gazillion residential services installed with aluminum. Why spend more money to do the same thing, when aluminum has already proven itself?
 

wawireguy

Senior Member
Honestly I really think copper and aluminum are inferior. What you really want is the platinum plated stuff. Much better than either.
 