DC and AC in the same conduit

Status
Not open for further replies.

jaggedben

Senior Member
Location
Northern California
Occupation
Solar and Energy Storage Installer
Here's one that's come up for me again...

In your opinion, is there anything in the NEC that prohibits running PV source and/or output circuits in the same conduit as the inverter output circuit for the same system? We are talking conduit, not a gutter, and thus no possibility of a partition. Let's limit it to 2008 or 2011.
 
Nothing prohibits this...partitions are not necessary for pv system conductors, even in a gutter. Conductors of each type of pv circuit just need to be "grouped". The partition is needed in gutters with non-pv conductors. That's how I sees it anyhow.
 