stew
- federal way,washington
If a concrete pad is poured to set a packaged spa on does the slab need any grounding? Cant really tell from the book if it is only required for pools or if also for spas.
680.42(B) Bonding. Bonding by metal-to-metal mounting on a common frame or base shall be permitted.
Exception No. 1: The metal bands or hoops used to secure wooden staves shall not be required to be bonded as required in 680.26.
Exception No. 2: A listed self-contained spa or hot tub that meets all of the following conditions shall not be required to have equipotential bonding of perimeter surfaces installed as required in 680.26(B)(2):
(1) Is installed in accordance with manufacturer?s instructions on or above grade.
(2) The vertical measurement from all permanent perimeter surfaces within 30 horizontal inches (76 cm) of the spa to the top rim of the spa is greater than 28 inches (71 cm).