meter & mast

Status
Not open for further replies.

John120/240

Senior Member
Location
Olathe, Kansas
If you have an overhead service, the mast connects to the meter thru a hub.

No extra bond required. Now connect a short rigid nipple from meter to

disconnect & bonding locknuts are required. Why the discrepancy ?
 

pete m.

Senior Member
Location
Ohio
I'm not sure that there is a discrepancy. Take for example a run of rigid conduit in a classified location. Is extra bonding methods required around each threaded coupling? The hub on the meter is esentially the same concept.

Pete
 

RUWired

Senior Member
Location
Pa.
Article 250.92(B) lists the method of bonding service equipment and raceways. Threaded hubs are approved for bonding the raceway to the meter base. With the nipple below, standard locknuts alone does not meet the requirement.

Rick
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
If the disconnect has a hub like the meter, bonding locknuts/bushings might not be required.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
If the disconnect has a hub like the meter, bonding locknuts/bushings might not be required.


It should have something like that if this is in a wet location. The hub would be permitted to bond the nipple since it would only require bonding on one end.
 