if the voltage across poles at dryer recep. is 215v the service voltage must be?

if the voltage across poles at dryer recep. is 215v the service voltage must be?


  • Total voters
    32
Status
Not open for further replies.
Why would you bring 480Y/277 to an apartment building, you would have transform 99% of it to 208Y/120 to use it. That burns up money and space.

It was mentioned 480Y/277 + 208Y/120 with transformer or TWO SERVICES.

Why would you bring in 480v?
Central chiller on roof or basement that provides cooling for all the building or buildings in complex. Running 4 fast elevators serving 40 stories. Parking facility lighting.
 
Apartment buildings can vary on incoming service based on when they were built. Newer ones are 277/480 or 120/208 as they are commercial. Older ones are 120/240 delta....I truly dislike the wild leg!

All single family homes around here are 120/240 services.

It was mentioned 480Y/277 + 208Y/120 with transformer or TWO SERVICES.

Why would you bring in 480v?
Central chiller on roof or basement that provides cooling for all the building or buildings in complex. Running 4 fast elevators serving 40 stories. Parking facility lighting.

That is not an apartment building it is a hotel where the guests stay for long time - even years:lol:

Seriously I can see the need to bring 277/480 into the building if it is a rather large building and especially if it has elevators, fire pump, centralized heating or cooling, and things like that.

I don't see much need for a 240 delta for apartment building. What are you going to use the wild leg for besides HVAC? Maybe in a rather large facility but then 277/480 again would likely make more sense.
 
It was mentioned 480Y/277 + 208Y/120 with transformer or TWO SERVICES.

Why would you bring in 480v?
Central chiller on roof or basement that provides cooling for all the building or buildings in complex. Running 4 fast elevators serving 40 stories. Parking facility lighting.



We do large buildings like that, all those items can run on 208.

A typical large hotel we have done may have a 4000 amp service.
 