according to Mike Holts NEC exam prep, you may not use table 310.15 (B) (6) to size the service conductors for a duplex because " table 310.15 (B) (6) is only for single family dwellings" but 310.15 (B)(6) says it's for single family, two family and multifamily dwellings, so if a duplex is not a two family dwelling, then what is?