plastic tubing in conduit

Status
Not open for further replies.

GlennH

Member
Was at a site today that had a day tank and pump control panel for a rain collection system. The control panel inside had a conduit run to the collection tank underground with wires for the submersible pump in the tank. It also had a 1/4 in. plastic tube in the conduit for measuring the depth of the water in the tank.

Aside from conduit fill concerns is this something the NEC addresses?
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
I think you can make a very good argument that this is not covered by 300.8 if it is just a sensing line.

And if you won the argument I wouldn't see a problem with it but, regardless of how well you presented your argument, I can see many if not most inspectors rejecting it based on 300.8.

Roger
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Wouldn't that only apply to Class 2 and 3 conductors, and not Class 1?

725.46 Class 1 Circuit Wiring Methods. Class 1 circuits
shall be installed in accordance with Part I of Article 300
and with the wiring methods from the appropriate articles
in Chapter 3.
Yes, it appears that 300.8 would apply to a Class 1 control circuit.
 