When testing a industrial site's ground grid is megging it the only test thats used? What test are used to check its integraty ?
 

edavis2293

Member
Location
Houston, Texas
Null Meter

Null Meter

When testing grounding resistance we use a null meter. The one I see most is made by Biddle. There are two (2) additional electrodes used but only about 12" long. Follow the directions that come with it, very easy to operate. As many times as I have used these, 25 ohms is not even close and a second electrode is required.
 

zog

Senior Member
Location
Charlotte, NC
When testing a industrial site's ground grid is megging it the only test thats used? What test are used to check its integraty ?

As mentioned you don't use a megger, you need to do a 3 point fall of potential test at several different distances from the grid to verify your measurements are accurate (Looking for a plateau). You also want to check all connections using a microhmeter. Your best bet is to contact a testing company that has the equipment, training, and procedures to perform this test.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
What are you trying to test? Are you really looking for a ground resistance test or are you looking to prove that every thing is bonded together?
 

hawkeye23

Senior Member
Location
stanton
There appears to be a lot of unsettling ground, dips and holes just concerned that there is not a problem with the underground cables.
 