I seem to have missed out on the discussion.  I would have liked to jump back in earlier.
Let me start by reminding everyone of the following type of disagreement, for I believe we are in the middle of just such a misunderstanding.
Rick, we are both wrong.  The total current is, in fact, neither 200 nor 600.  The total current is zero, and will always be zero regardless of power factors, phase angles, or the degree to which the loads are balanced.  Kirchhoff’s Current Law demands that it be zero.
That said, I think we need to get our use of terminology settled out, for one of us is talking about the color of the sky, and the other is talking about the color of the grass.  I do not like the use of the word “total,” in the context of currents flowing in more than one phase.  I particularly dislike the use of the word “per” within the phrase “amps per phase.”  These two words, I do believe, are the cause of the misunderstandings and disagreements on display in this thread and in many other discussions as well.
Let us consider a three phase panel with a three phase main breaker that has a load on each phase (note, I did not say “load per phase”) of 200 amps.  Let us consider all loads to be single phase, and purely resistive in nature.
?         You have asserted that this represents a total of 600 amps of single phase loads.
?         I agree, and I have not said anything that contradicts that assertion.
?         I submit that it is inappropriate to describe this situation by stating that “the total load on the breaker is 600 amps.”  Indeed, I believe the phrase “total load” has no meaning.  One reason is that this same panel could have, instead of a bunch of single phase loads, one load that is a three phase load that draws 200 amps from each phase.  The main breaker could not distinguish this situation from the single phase loading situation.  But I don’t think you would say that this solitary three phase load represents a total load of 600 amps.
?         I have asserted (in essence, but using different words) that the current leaving the main breaker (i.e., on its way to the panel’s bus bars) on Phase A will return to the breaker on Phases B and C.  I have further asserted that it is all “the same current.”  You have not contradicted that assertion, and I am confident that you would agree.
?         I have (begrudgingly) used the statement “the total load is 200” to describe this situation.  Despite my objections to that phrase “total load,” many people continue to use it.
In conclusion, whenever we hear or see anyone using the phrase “total load,” I think we should call a “time out,” and ask the person to clarify what they intend that phrase to mean, before we attempt to answer any questions.