A load center on structure ?A? has a 3-pole 100A rated circuit breaker protecting #2awg conductors that are feeding a 200A MCB at a separate structure called structure ?B?. Is this a NEC Code violation? If so, which specific codes? 
The continuous load and non-continuous load is not a factor. The total demand for structure ?B? is 30A per phase. The 200A panel at structure ?B? is an existing panel and is presently being fed with a small generator. The generator is being removed and structure ?B? is going to be powered by structure ?A? which is fed by the utility.
	
		
			
		
		
	
				
			The continuous load and non-continuous load is not a factor. The total demand for structure ?B? is 30A per phase. The 200A panel at structure ?B? is an existing panel and is presently being fed with a small generator. The generator is being removed and structure ?B? is going to be powered by structure ?A? which is fed by the utility.
				