generator question

Status
Not open for further replies.

Hendrix

Senior Member
Location
New England
answers to my post have dissapeared:cry:
however, I have another question. When can one use the "round up" method of determining the size of the conductors versus amperage with a generator? To be more clear.... can one use 500kcm conducors and fuse at 400 amps using the round up method from 380 amps?
 
Last edited:
on the load side of your generator OCP device you can as long as your calculated load does not exceed the conductor ampacity,
 