Im working on a large house with a detached garage. The detached garage is required to have a few branch circuits for the lights, receptacles & opener etc.
Would it be possible to feed these circuits from a panel in the main house?
225.30 Number of Supplies. A building or other structure
that is served by a branch circuit or feeder on the load side
of a service disconnecting means shall be supplied by only
one feeder or branch circuit unless permitted in 225.30(A)
through (E). For the purpose of this section, a multiwire
branch circuit shall be considered a single circuit.
Where a branch circuit or feeder originates in these
additional buildings or other structures, only one feeder or
branch circuit shall be permitted to supply power back to
the original building or structure, unless permitted in
225.30(A) through (E).
For the purpose of this section, a multiwire branch circuit
I'd imagine that a feeder from the house's panel would be a cheaper superior design. Branching the service for this task seems a little fruity and would complicate changing needs in the future, IMO.
What is wrong with 200 amp meter socket, conductors sized for calculated load (of 200 amps max) for both structures. From socket go to a terminal or splice box if you can't come up with meter with double lugs and go separate ways from there?
Done it that way also.
It may be easier or even cost less to use 320 socket but that is an option.
A 200 class meter will plug into a 320 socket won't it? If not that could bring up issue with POCO. The supply to the 320 socket will not have to be more than 200 amp conductor if calculated load is not over 200 amps. Some people have a hard time realizing that.