swptln
Member
- Location
- East Brookfield, MA
It's been a long time since I wired a pool, correct me if I'm wrong, but my take on the 680.26 EB for an aboveground permenant pool, is if the pool has a vinyl liner, 680.26(B)(1) or (2) do not apply.
Now, what if this pool has an aluminum wall with a NM frame??
Does this wall need to be part of the EB? or when I run my #8 around the pool per 680.26(B)(2)(b)(1-5) should I bond the wall at 4 points??? even though the pool has a nonconductive shell.
Mark
Now, what if this pool has an aluminum wall with a NM frame??
Does this wall need to be part of the EB? or when I run my #8 around the pool per 680.26(B)(2)(b)(1-5) should I bond the wall at 4 points??? even though the pool has a nonconductive shell.
Mark