Homeline 2-pole lock-on?
George Stolz
Windsor, CO NEC: 2017
Service Manager
I'm needing a breaker lock to hold a breaker on without a padlock for a APS. the best the supply guy can find is a hom1hbd which says it locks the breaker off. Anybody see one of these firsthand to tell me if I can flip it over and use it to lock a breaker on?
sameguy
New York
Master Elec./JW retired
What breaker is it.
QO type:
look at, qohpl, qo1pa, qothpa, qo1hpl
found pg.1-4 Schneider book
jim dungar
Wisconsin
PE (Retired) - Power Systems
A xxxxHBD is for blocking a breaker off.
A HOMxPA is for padlocking a breaker on or off.
A QO1LO can be used to 'clamp' a HOM 1P On or off.
See Digest 175 page 1-14 table 1.42
480sparky
Iowegia
A standard, run-on-the-mill, plain-jane 2-pole lockout won't work?
That is why the QO line is superior. Much bigger variety of accessories.
Epoxy the handle in the on position, if breaker ever trips you will need to replace instead of reset:D