kingpb
- SE USA as far as you can go
- Engineer, Registered
Don't ever try to understand the logic of a utility company. It is layers and layers of bureaucracy and different departments that don't talk to each other.
I don't know if it *is* open delta; I'm going to reach out to their transformer expert & see what he says.
Of course, if it's closed delta, that just furthers my confusion as to why a wye installation is Special Facilities but a delta is not.
Don't ever try to understand the logic of a utility company. It is layers and layers of bureaucracy and different departments that don't talk to each other.![]()
It could be something as simple as equipment they have lying around that they want to get rid of vs. gear they have to special order and buy.Don't ever try to understand the logic of a utility company. It is layers and layers of bureaucracy and different departments that don't talk to each other.![]()
Are you sure? I thought you had to use some sort of rotating mechanical device to make three phase out of split phase. Or is there already three phase power to the site?exactly.
120/240 single phase transformers are the most common ones they have in stock. They can easily be used to build a delta transformer bank, both open and closed delta. You can easily add one to an existing setup to gain a third phase.
Yep.... you just have design your end accordingly.
If by split phase, you mean what what otherwise be called single phase 3 wire, then yes mechanical rotating machinery, or electronic converting plant is required to produce 3 phase.
In this case though it appears safe to asume that the utility has 3 phase at MV available.
Therefore 3 phase open delta via 2 transformers, or 3 phase closed delta via 3 transformers is a simple matter.
3 phase delta service at 120/240 volt is often regarded as obsolete or old fashioned, but has its merits.
Standard transformers all with a center tap on the secondary are used, but obviously only one center tap may be grounded.
First off, this transformer [?bank] will be for my clients house & pool period. It's a 1400 ft run {their route} from their pole lines [3ph 21KV w/Neutral]. He's paying {seemingly insane amounts} for the service because of that. I have no idea if they will spec 2 pad xfmrs or one 3-ph; but they will be pad mount; it's underground service.
The Greenbook Table 9 lists a 25/10KVA transformer #261547 with 240/120 out. Does that mean the stinger leg is 25KVA and the other two are 10, maybe?
Yes/no/maybe
First, I'm trying to picture the situation. The primary is 20780VGrnY/12000V.
[BTW: the single-phase quote is $29K; 208 wye $60K]
I don't know if they will run open delta or not. Assume they do; so they use both shields {as I'd call it with coax cable..} in parallel for the neutral. Is that also the neutral on the centertapped secondary; or is that just a local creation with a ground grid?
Assuming they don't; they bring in all three phases & don't need a neutral on the transformer primary.
The complications of this will be from the solar and appliance aspects. I'd assume we'd want to push bigger 240v loads to non-centertap sides. That means we have to get "really 240" not 240/120 range top, oven, dryer, sauna, heat pumps. More research.
Also, we can only have a backup inverter on the 240/120 leg. While the gridtie inverter are happy with stinger systems, the backup inverters are 120-only in the US.
THAT means, during an outage, only a third of the PV arrays are working. [The gridtie inverters will 'follow' the PoCo line OR when up, the backup inverter.} That's a loss, as we hope PV input will keep propane usage by the generator to a minimum.
B
A g C
The A-N-C secondary got the term "lighter" early in adoption of open-delta services because the lighting load was only L-N. Not sure how "stinger" was coined.Heard back from my new best friend, a senior PGE engineer.
Yes, they supply open delta in cases such as this. Poles, they hang two single ∅ units; on pad-mounts, their term is a "duplex" transformer. Using my
Code:B A g C
where AgC and BC windings exist, but BC is open; they call AgC the "lighter" secondary as it supplies most of the load. The B terminal is the "stinger"; I had that backwards.
I understand the issues re: future range replacements, but setting that aside; do I strive to put the 240V loads only on A-B; or also on B-C? [B is the "stinger terminal" but are both A-B & B-C "stinger legs" or not?
How concerned should I be about balance on the 3-phase loads; and what do we do if they are not? Rotate connections, etc. but what's above that?
What about harmonics? We depend on deltas for suppression; here we lose that? or do we?
Good point.I would use single phase panels for most of the lighting/general loads. If you use three phase panels here you will have a lot of open spaces where the wild leg is.
I would only run three phase to areas where you will use it and also run some of the HVAC, water heater, well pump and other similar loads that can utilize the wild leg to a three phase panel.
An open delta system has a greater capacity for 1? loads connected across the stinger winding. This is because current of 1? loads connected across the open terminals has to travel through both the lighter and the stinger windings. Capacity is calculated for equal loading A-B and B-C.
See page 9 of this Cooper publication:Can one of you smart guys post the picture of the open delta secondary and explain this via that picture so us not-so-smart guys can learn something?
I am confused which winding you are referring to as the 'stinger' winding.
I know and have serviced this type of system, but I want the low down on it as far as the capacities of each phase.
Thanks