Need some ideas on what may be happening. The new equipment and system is as follows: Three 480V 30hp fans, 6 awg wires are used each connected to a GECR306E1 starter and then connected to Eaton 80amp E125S breakers in a 400amp panel. The panel serves all 3phases loads including 3 elevators. The problem is fan #1 trips the breaker on start up randomly up to 50% of the time. The heaters in the starter have not tripped. There have been no issues with the other two fans. The fans stage on in 5-10 sec steps. So we thought it could be something to do with the order so that was changed and fan #1 breaker trips no matter the start order. The fan motor was replaced and the breaker continued to trip. The breaker was switched with a spare breaker. Breaker would still trip. Now for the really confusing part, all three fan breakers are on the right side of the panel starting at the top with Fan #1(problem circuit). If fan#1 wires are moved to fan #2 breaker (next breaker down) and #2 is moved to #1 breaker the problem goes away??. Any ideas?