Pool Ladder Stray Voltage

Status
Not open for further replies.
Got a call today from an home owner saying that when they turn the microwave on, they are getting shocked on the pool ladder. They have (2) metal ladders but its just on one they get shocked on. Checked voltage to ground and the ladder had 4 volts. It only happens when the microwave is on. I havent had time to troubleshoot it all the way yet. Just want some insight on what it could be. Thanks
 

stickboy1375

Senior Member
Location
Litchfield, CT
Got a call today from an home owner saying that when they turn the microwave on, they are getting shocked on the pool ladder. They have (2) metal ladders but its just on one they get shocked on. Checked voltage to ground and the ladder had 4 volts. It only happens when the microwave is on. I havent had time to troubleshoot it all the way yet. Just want some insight on what it could be. Thanks

bond the ladder.
 

satcom

Senior Member
bond the ladder.

It may already be bonded, stray is a funny duck, you can have the best bonding job and still have stray present, we have areas where entire developments can't use their pools because the stray current is high, the power company has been working on the problem for some time, short of re designing the local distribution network they tried additional grounding as some of the sub stations with limited success, some engineers feel the distribution return feeds are part of the problem, so if you bond and the problem continues, check to see if there are other pool users in the area with the same problem.
 

stickboy1375

Senior Member
Location
Litchfield, CT
It may already be bonded, stray is a funny duck, you can have the best bonding job and still have stray present, we have areas where entire developments can't use their pools because the stray current is high, the power company has been working on the problem for some time, short of re designing the local distribution network they tried additional grounding as some of the sub stations with limited success, some engineers feel the distribution return feeds are part of the problem, so if you bond and the problem continues, check to see if there are other pool users in the area with the same problem.


good video to watch....
http://www.mikeholt.com/strayVoltageVideo.php
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Are there any other electrical issues in the house? Voltage on the ladder only when something is turned on would have me thinking of a neutral problem.
 

wirenut1980

Senior Member
Location
Plainfield, IN
Could be a neutral problem. The problem may manifest itself with a large single phase load turned on, which a microwave is one of the largest in a house. A hairdryer would be another. This type of load would result in a larger than normal neutral current. 4 V does not scream to me there is a neutral problem or secondary fault. Proper bonding of the ladder should fix the problem.
 

satcom

Senior Member
Are there any other electrical issues in the house? Voltage on the ladder only when something is turned on would have me thinking of a neutral problem.

Yes it could be a local neutral problem and it also may be the return feed to the sub distribution needs to be sized up, he has some trouble shoots to do, and questions to ask
 

wirenut1980

Senior Member
Location
Plainfield, IN
It does to me, if the voltage is only there when the microwave or other large load is turned on.

It may make the voltage on the ladder go away, but it does not fix the problem.

I would agree if there was no voltage with the microwave off.

If I put 15 amps from a microwave on the neutral with a impedance of 0.1 ohms, that is 1.5 V added to whatever voltage is already existing due to primary neutral voltage drop. I think this is the more likely scenario. It would be interesting to see what the voltage measured is without the microwave on.
 

satcom

Senior Member
Mikes video on stray is excellent, I had an old westinghouse engineer explain it to me back in the 70's mikes video is right on.

Yes Don, locating the problem is not always that easy, one pool we had stray problems with turned out to be a boot leg neutral connection in a kitchen wall switch, some master hack installed recess lighting, and since there was no neutral in the switch box he ran the recess lighting neutral to the metal switch box (Bootleg) and when his daughter had her hair drier on, his wife felt the tingle in the pool.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
I would agree if there was no voltage with the microwave off.

If I put 15 amps from a microwave on the neutral with a impedance of 0.1 ohms, that is 1.5 V added to whatever voltage is already existing due to primary neutral voltage drop. I think this is the more likely scenario. It would be interesting to see what the voltage measured is without the microwave on.
I think that only the additional voltage drop on the line side of the main bonding jumper would show up between the bonded pool parts and unbonded parts.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician

goldstar

Senior Member
Location
New Jersey
Occupation
Electrical Contractor
That was a step potential caused by a damaged 480 volt feeder. The fault current was not high enough to trip the OCPD but it set up a fatal step potential in the ground.
Don, I didn't see any follow-up stories on this. If you have a link to news clip would you please post it. I can't imagine why this failure could not have been detected long before the tragedy occurred.

Thanks,

Phil
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Don, I didn't see any follow-up stories on this. If you have a link to news clip would you please post it. I can't imagine why this failure could not have been detected long before the tragedy occurred.

Thanks,

Phil
I don't have any links...the irrigation system feeder was damaged by lightning the day before and an electrician was on his way to check out the problem when the tragedy happened. At least this is what I have been told from some unofficial sources. I don't think we will have any firm details until the OSHA report is released 6 to 12 months from now.
 