- Lockport, IL
- Semi-Retired Electrical Engineer
Common information for all three: Transformer within outdoor substation. Cables connect secondary to busbars. Breakers serve loads both inside and outside the adjacent building. Primary is over 600 volts, secondary is 120/208V.
Question:
Table 450.3(A) allows us to double the rating of the secondary protection for supervised locations. Why? If you overload something, it is going to fail, so what difference does supervision make? And how does the qualification of a future maintenance worker affect the performance of a transformer that is, here and now, being overloaded? What I really want to know is how do I take advantage of the 250% factor? Do I have to install sensors, so that a ?qualified person? has the ability to ?monitor? the transformer?
Question: