We are building a PV system on the landfill. The primary wiring will come from the road encased in concrete. We are constructing a pad on the landfill for our inverters, transformers, CT cabinets etc where the primary will land. This pad will have a ground ring and grounding plates.
Why both?
I am concerned about grounding at the PV arrays. There could be over 400 feet between the panels and inverter and I want to provide local grounding electrodes at several points within the array.
Why do you want to ground the PV arrays? Is there some non-obvious benefit to doing so?
The landfill only has 6" of soil above it's PVC cap and we can not penetrate this cap. The code gives a minimum cover for ground plates of 30" but we don't typically have 30" of soil unless we mound it above the plate.
So mound it. It is just dirt.
We do have 12' concrete ballast blocks with rebar sitting on the ground that could perhaps be looked at as a U-fer ground.
They may well be a perfectly good means of grounding but I don't know that they meet the requirements for a GE. OTOH, if you are talking about ballast blocks for the PV arrays I don't know that they require a GES anyway so feel free to connect right up.
Any suggestions for this local grounding?