Hello all,
1) Customer owned padmount Wye-Wye primary transformer: Primary was not served a neutral. I know I can leave X0-to-case strap, install another MBJ at the load's main disconnect & run PVC with no ground to the load's main disconnect per 250.30(A)(1)Ex2. I believe H0 should still be strapped to X0 because of the lack of primary neutral. Would this still be a SDS?
2) If the primary neutral IS served to the transformer, should H0 and X0 still be connected? Since a primary neutral is served, would THIS be a SDS as H0 would be direct tied to X0? Also, I don't think you would ever want to bond H0 to the case.
3) What differences would it make if this transformer were utility owned? Can I still invoke the same 250.30(A)(1)Ex2 load-side installation technique?
Thanks for reading.
I used the word 'neutral' rather than 'grounded conductor' for ease of reading.
Thanks for reading.