Assuming they all have magnetic motor starters it's as easy as breaking the control power through a phase monitor relay or relays. It depends on whether they want the whole facility protected or protection at each motor.
There aren't any starters from the answers I got from the A/C tech. It will be protecting individual motors.
Can you point me to an example of a phase monitor relay.
I am going to look at a job where the customer wants to protect their motors from single phasing. What kind of set ups or equipment do you use?
Most electronic motor overload relays also trip upon single phasing.
Careful selection of thermal overload relays will also protect from single phasing but will have slower response time. If you lose a phase, current in other two will increase and overload will trip.
If you want to shut off an entire machine immediately upon phase loss then use some of the phase monitors people have suggested. You don't interrupt motor current with these, you open a control circuit.
I think they have had problems in the past with the heaters not working fast enough and allowing the motor to keep running (and fail.)
Thanks for all the suggestions.
Just something else to remember, make sure when you install the phase monitor it doesn't shortcycle the motor if the power fluctuates. You need it to drop out the motor and keep it off.
If overload heater is sized properly it will protect the motor. I still have better faith in thermal overloads than electronic, but they do have to be selected properly. If selected properly rise in temperature of the overload element will be similar to rise in temperature of motor windings.
Seen too many electronic overloads get turned to highest possible setting and not properly protect motor. At least with thermal elements you have to do more than just turn a dial. I have seen many electronic overloads just plain fail. Siemens seems to be the worst. Thermal elements will withstand more adverse conditions.
I would think there could be situations where the overload would not trip and motors could still overheat due to running for a long time on over 100% rated FLA. It really depends on how loaded the motor is before getting single phased, and what % of FLA the overload is set.
I do not know of a major NEMA manufacturer (Rockwell, Schneider, GE, Eaton, Siemens) of overload relays that says their standard thermal offering will protect motors against single phasing. While they all do sell thermal overloads that have single phase sensitivity, for critical applications they usually recommend you use a dedicated type 'phase loss relay'.If overload heater is sized properly it will protect the motor. I still have better faith in thermal overloads than electronic, but they do have to be selected properly. If selected properly rise in temperature of the overload element will be similar to rise in temperature of motor windings.
Good for you.I have seen many thermal overloads trip under single phasing conditions.