Exhaust Fan In Shower Space
infinity
New Jersey
Journeyman Electrician
I don't know how these simple questions can get so convoluted.
What fun would it be if you had only one word answers. :roll:
I will try it:
Since arc fault breakers offer about 30ma of ground fault protection, would that satisfy the manufacturers requirement for GFCI protection for exhaust fans within a shower space?
NO.
DARUSA
New York City
But what about if the bathroom is a master bathroom Do I need arc fault for the lights and also GFCI for the outlet?
Can I just run a line for the GFCI and the exhaust and pick the lights from the bedroom circuit?
John120/240
Olathe, Kansas
Master bathroom, kids bathroom it Doesn't Matter. You still need
a seperate 20 A GFCI recptacle from adjacent bath or it's own circuit. Exhaust
fan over the shower or shower light need whatever protection is specified in
installation instructions. General purpose lights have no special requirements.
If you need GFCI protection for shower light/fan install a faceless GFCI between
the switch & fixture.
DARUSA
New York City
Ok but if you have a walking closet in your room and have lights and outlet in it ,Do you have to have ARCFault protection in all your 120 volts loads? I say yes!
Do the bathroom need the same logic?
GFCI outlet is clear but do your lights need to be arc fault protected?
Twoskinsoneman
West Virginia, USA NEC: 2020
Facility Senior Electrician
Yes... closets require AFCI.... Bathrooms do not...
What is the issue?
al hildenbrand
Minnesota
Electrical Contractor, Electrical Consultant, Electrical Engineer
No to the AFCI, Yes to the GFCI
Yes
You do not "need" to put the lights on an AFCI, but you "can, if you want."
You can put the lights on the 20A line with the receptacle and the fan, if you want, also.