Have a call to go to tomorrow where the customer says the Leviton single pole slide dimmer in her kitchen is getting hot after the lights haev been on all day. We just installed this a couple of months ago. It is in a 2 gang box with another dimmer. The one getting hot is rated for 600W (500W when installed in a box with 2 dimmers). It has 6 five inch recessed cans with 50W R20 flood lamps in each can for a total of 300W total load.
I don't really want to have to go to a 1000W dimmer if I can avoid it.
Any suggestions as far as things to suspect for the cause?
No the connections aren't loose.