700.12(D) Fire Protection. Emergency systems shall meet the
additional requirements in (D)(1) through (D)(3) in assembly
occupancies for not less than 1000 persons or in buildings
above 23 m (75 ft) in height with any of the following
occupancy classes: assembly, educational, residential, detention
and correctional, business, and mercantile.
Informational Note: For the definition of Occupancy Classification,
see Section 6.1 of NFPA 101-2009, Life Safety
Code.
(1)Emergency Systems shall meet the additional requirements in
(D)(1) through (D)(3)
(1) Be a listed electrical circuit protective system with a minimum
2-hour fire rating
Informational Note: UL guide information for electrical
circuit protective systems (FHIT) contains information on
proper installation requirements to maintain the fire rating.
(2) Be protected by a listed thermal barrier system for electrical
system components with a minimum 2-hour fire
rating
(3) Be protected by a listed fire-rated assembly that has a
minimum fire rating of 2 hours and contains only emergency
wiring circuits.
(4) Be encased in a minimum of 50 mm (2 in.) of concrete