When wiring lighting fixtures, say a row of six, which article of NEC applies or prohibits the use of #18 AWG wire?
			Welcome to the forum.
310.5 shows the minimum sized conductors that can be used as a general rule. #14 AWG copper is the smallest branch circuit conductor you can run.
Now Fixture wires are permitted to be #18 AWG (See 402.6) but if you are daisy chaining 6 fixtures together the conductors that you are using to connect the fixtures together would be branch circuit conductors.
Chris
Would 210.19(A)(4) apply also?