i understand this article when installing multi wire branch circuits.
question what if let say you install 6 circuits with 6 neutral in the same conduit entering a panel .does each circuit and neutral have to be identify as they enter a panel cant find where it says that.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
It really is not different than 6 mc cables entering the panel. Now I believe each neutral should be identified with the appropriate ungrounded conductor.
 

Twoskinsoneman

Senior Member
Location
West Virginia, USA NEC: 2020
Occupation
Facility Senior Electrician
i understand this article when installing multi wire branch circuits.
question what if let say you install 6 circuits with 6 neutral in the same conduit entering a panel .does each circuit and neutral have to be identify as they enter a panel cant find where it says that.

That does not apply to the two-wire circuits mentioned in the OP.

Fooled by the title of the thread saying 210.4 :D
 