Secondary Current Calculations
A quick and dirty way would be to convert the primary measurements to watts and use that to figure the secondary current.
Of course this will show only the average phase current not the actual current and does not account for transformer losses.
I have a quicker and dirtier way:p:
Take the Pri/Sec voltage ratio and mulitply the primary current with it.
Ex: 480/208= 2.308
75kVA Transformer FLA
480V Pri: 90.2
208 Sec. 90.2*2.038=208.15A
If I have the primary currents (unbalanced) of a delta-wye transformer how do I calculate the secondary currents? An example would be helpful
To calculate the unbalanced secondary currents with any accuracy, I think you will also need to know the phase angle of the primary currents.
Yes I will know the primary currents and phase angles of IA and IC, but not IB. I want to know if there is a way to get the secondary currents and phase angles Ia, Ib, and Ic. Or are there just too many unknown variables?
Knowing all three primary current magnitudes and phase angles is necessary for calculating secondary currents... and that is if it is possible.
When metering power (kW) or electrical energy (kWh), Blondel?s theorem states that total power for a system containing N conductors that it can be correctly metered with N-1 single phase watt-meter elements (Voltage x current). It is standard practice for a ?delta primary transformer? (ex. 416V 3ph/3w to 120/208V 3ph/4w) to install 2 current sensors (CTs), one on A and one on C phase (i.e. I_A and I_C), and connect the voltage measurement from phases with CTs to the phase without CTs (i.e. V_AB and V_CB).
NOTE: I am using capital letters (A, B, C) for primary values and lower-case letters (a, b, c) for secondary values.
Ignoring losses due to transformer efficiency, by conservation of energy, the power on the primary must therefore be equal to the power on the secondary. Therefore:
Power In = Power Out
(V_AB) (I_A) (Cos θ_AB) + (V_CB) (I_C) (Cos θ_CB) = (V_a) (I_a) (Cos θ_a) + (V_b) (I_b) (Cos θ_b) + (V_c) (I_c) (Cos θ_c)
NOTE: θ_AB is the phase angle between V_AB and I_A (+ 30 degrees for a resistive load) and θ_CB is the phase angle between V_CB and I_C (? 30 degrees for a resistive load)
What I want to know is the secondary currents (I_a, I_b and I_c) and phase angles (θ_a, θ_b and θ_c) in order to determine if the load is balanced. I want to do this using existing ?delta-connected? electricity meters that are readable from a remote location (AMR) to do this analysis.
Approaching from a power in, power out perspective doesn't account for reactive power (i.e. current is out-of-phase with the voltage).
I'm 30 plus years from putting Blondel's Theorem into practice... so doing a refresher is not going to happen on this end. But what I will do is suggest a course of evaluation. That is to first attempt your method of calculation using a delta-wye one-to-one winding ratio transformer configuration... which is actually a stepup transformer. As such, your winding currents and voltages will be the same for input and output, making the calc easier.