Commercial Retail Store Calc
rgiraldo
FL
just want to check to see if I am correct.
Continuous Loads
4000 sqft @ 3va per ft 12000va
Show Window- 30ft @ 200va per ft 6000va
Sign 1200va
19200va X 1.25 = 24000va
Non-continuous Loads
76 receptacles @ 180va 13680va
First 10000va @ 100% 10000va
Remain 13680-10000=3680x50% 1840va
11840va
Air conditioner #1 6900va
Air conditioner #2 6900va
Cylinder Machine #1 1500va
Cylinder Machine #2 1500va
Compressor + 25% 2500va
Water Heater 3000va
Total Volt Amps 58140/240=242.25a
Panel @ 400a
Breaker @350a
Where can I cut the fat to keep it under 300A total?????
Please let me know if I missed a step or missed a reduction some where
Panel @ 400a
Breaker @350a
Not sure I understand the question. You can put this a 250A MCB panel with a 250mcm (cu) feeder.
I thought the breaker needed to be upsize 25% for continuous loads. Or did I all ready do that with my general lighting.?
You already did that. Your breaker needs to be larger than 100% of your non-continuous loads plus 125% of your continuous loads. (See 215.3.)
As your calc shows, that's 242.25A, so a 250A c/b meets the requirement in 215.3.
My understanding is that panel bus bar must equal load amp and main panel breaker x 1.25%.
Your panel bus bars must be protected with OCPD greater than or equal to the bus bar ratings. (See 408.36.)