K KWH Senior Member Aug 7, 2011 #1 I have a 600 Main breaker MDP. The connected load is 409 amps, 400al. xhhw would suffice in this situation or would it.
chris kennedy Senior Member Location Miami Fla. Occupation Retired electrician Aug 7, 2011 #2 Show us how you came up with that.
Dennis Alwon Moderator Staff member Location Chapel Hill, NC Occupation Retired Electrical Contractor Aug 7, 2011 #3 Are you trying to size the wire that feeds the main distribution 600 amp breaker? or are you feeding from the 600 to a panel with 409 amp load? I also would love to hear how 400AL will work.
K KWH Senior Member Aug 7, 2011 #4 Forgot to mention parralled Forgot to mention parralled The 400 al would be x 2 runs sorry about that
augie47 Moderator Staff member Location Tennessee Occupation State Electrical Inspector (Retired) Aug 7, 2011 #5 It would be Code compliant.
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician (retired) Aug 7, 2011 #6 KWH said: The 400 al would be x 2 runs sorry about that Click to expand... They would need to be in separate raceways to be compliant unless you were using a wireway.