1793
- Louisville, Kentucky
- Inspector
I could really use the help of others with a problem I'm having with a Multiwire Branch Circuit.
Situation:
2 story Pool House wired with all MWBC.
Outside 2 gang receptacles ( Red to GFI and Black to GFI )
Both receptacles quit working
I was called to investigate and I can not figure out this one.
Voltage, using DMM,
R-N=35
B-N=35
R-B=0
R and or B to ground 35.
The only way I can get 0.00 reading is to turn off breakers 5 & 7 and 8 & 10.
Breakers 5 & 7 are both Black and breakers 8 & 10 are R / B.
Turning off other combinations of breakers yields lower and different readings.
I'm stumped
Situation:
Voltage, using DMM,
R-N=35
B-N=35
R-B=0
I'm stumped