branch circuit cal
a dwelling unit kitchen has the follwing applicances : 9kw cooktop and one wall mouted oven rated 5.3 kw. the branch circuit calculated load for these applicance is
I use table 220.55 columm c for cooktop=8kw
columm b for wallmount=5.4x80%=4.3
8kw+4.3kw= 12.3kw round off =12kw
open for suggestion if my calculation is incorrect
thanks
look at 220.55, note 4. See if it doesn't interest you. By the way, which test are you studying for?
thanks
I agree with Hv&Lv. Since you said branch circuit, note #4 can be used.
just want to learn more
I am in school study load calculation. how ever the sample in class is very simple. so I am just to find more interest problems. however all my calculation result are too much compared to the answer.
so I want to learn more example and exception to different rule in NEC article
thanks
thanks
Do you understand what Hv&Lv means by looking at 220.55 note 4?