- Chapel Hill, NC
- Retired Electrical Contractor
Here is my proposal and substantiation-- what say you???  The red is what I added.
Here is my substantiation
			225.36 Suitable for Service Equipment. The disconnecting means specified in 225.31 shall be suitable for use as service equipment.
Exception: For garages and outbuildings on residential property, a snap switch, or a set of 3-way or 4-way snap switches, or other approved non service rated disconnect shall be permitted as the disconnecting means.
As this section is written I can run a multiwire branch circuit to a dwelling garage and use a DP snap switch as a disconnect but I can be rejected for using a non-fused disconnect such as an a/c pullout style disconnect. These a/c disconnects are not usually service rated. Why would a disconnect need to be service rated if one can use a snap switch? This proposal will help clarify what I believe to be the intent of this section. I realize this may seem petty but I know of a few people who have been rejected for this install.
