For a design consideration I am trying to determine what would be the cheaper cost between running one conduit with upsized (for de-rating) conducotrs or two sets of conduit for with the circuits split up between conduits.

So my two options are:

1) Run (1) 1-1/4" conduit with (4) circuits sized at #4 to account for de-rating with conduit fill and temp.

2) Run (2) 1" conduits with (2) circuits each sized at #8 to account for de-rating with conduit fill and temp.

I would think because of the cost of copper that running the two conduits in option #2 would be the least costly but I'm not exactly sure how the cost and labor for conduit factor into this?

Can anyone offer a suggestion?

By the way the 4 circuits are idential at 30A and in the same location.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
You need to do a cost analysis of the two. Don't forget the extra labor to run the extra conduit. Off the top of my head I would say choice one is cheaper.
 

iwire

Moderator
Staff member
Location
Massachusetts
I would (and have) done what Dennis suggests

In my case for 400 amp feeders two conduits and two sets worked out much cheaper than one conduit and one large set.