 - Tennessee NEC:2017
 - Semi-Retired Electrician
Gus, you done it again!:lol:
But who won?:?
			But who won?:?
Actually Table 310.16 is a very specific set of ?conditionof use? for ??Insulated Conductors Rated 0 Through 2000Volts, 60?C Through 90?C (140?F Through 194?F), Not More Than Three Current-Carrying Conductors in Raceway, Cable, or Earth (Directly Buried), Based on Ambient Temperature of 30?C (86?F).? Section 310.15 is a set of rules for appropriately adjusting the Table. As 310.15(A)(2) FPN mentions, 110.14(C) is part of the set.
Side note: When I first Proposed what is essentially the FPN, the CMP rejected it with a statement that was essentially, "Well that's just obvious."
I Happen to agree with you; "obvious" was essentially the CMP's statement. I proposed a more definitive statement. The FPN came a few cycles later. FPNs aren't enforceable anyway.Not so obvious as black and white, and the FPN just makes it more a medium shade of gray :roll:
And look where the FPN is, right after an exception which technically allows us to use the 90?C ampacity, because the termination is defiinitely less than 10 ft and most likely less than 10% of the circuit length at the higher ampacity. So if 110.14(C) is actually a conductor ampacity adjustment, then we can legitimately use 310.15(A)(2) Exception to get around it. So which is it???
I think the ampacity of the conductor comes from the table that lists the ampacity of various types of conductors. The ampacity of the conductor can be adjusted downwards for various reasons, but no where in the tap rules does it say that the ampacity mentioned in the tap rules is the adjusted ampacity.
I vote for 90 deg C column for THHN.
For others, exactly what are we doing here under 240.21(B)(2)? Are we not doing an ampacity adjustment where "The ampacity of the tap conductors is not less than one-third of the rating of the overcurrent device protecting the feeder conductors."?....
Temperature Limitations The temperature rating associated with the ampacity of a conductor shall be selected and coordinated so as not to exceed the lowest temperature rating of any connected termination, conductor, or device. Conductors with temperature ratings higher than specified for terminations shall be permitted to be used for ampacity adjustment, correction, or both.
We are to determine the ampacity of the conductor at the tap based on the termination's temperature rating. At the tap, only the conductor's size is relevant, not its temperature rating - unless it is lower than the termination's.... Are we not doing an ampacity adjustment ...
That's not too likely at all.... Consider that the tap connection may likely be made using a 90?C or better rated method...
You can stress the point however you want to no avail. I would agree with you totally if the wording explicitly supported your perspective. However, current NEC wording does not. I can see nowhere in the NEC that states 110.14(C) stipulations actually change the ampacity of an insulated wire conductor. In the meantime, I have no problem with operating under the assumed intent. But as long as the wording stays the same, I will continue to argue the point.We are to determine the ampacity of the conductor at the tap based on the termination's temperature rating. At the tap, only the conductor's size is relevant, not its temperature rating - unless it is lower than the termination's.
So termination temperature rating at the tap equal or better than conductor temperature rating means, from the perspective of conductor protection, the full ampacity value (e.g. 90?C column value adjusted per 310.15) can be used for the 1/3 ampacity determination, right?I need to back peddle. If the termination has a temperature rating equal or greater than the conductor's, it has no effective difference.
NEC wording in both 110.14(C) and by reference via 110.3(B) require it. (I already cited the UL reference.) SO- If you want to say 310.15 doesn't say it explicitly you are right. If you want to say the NEC doesn't require it - you are wrong; it just doesn't require it in 310.15. {That was what I tried to get the CMP to see - eventually they added the FPN to "remind" folks about 110.14(C)}You can stress the point however you want to no avail. I would agree with you totally if the wording explicitly supported your perspective. However, current NEC wording does not. I can see nowhere in the NEC that states 110.14(C) stipulations actually change the ampacity of an insulated wire conductor. In the meantime, I have no problem with operating under the assumed intent. But as long as the wording stays the same, I will continue to argue the point.
YESSo termination temperature rating at the tap equal or better than conductor temperature rating means, from the perspective of conductor protection, the full ampacity value (e.g. 90?C column value adjusted per 310.15) can be used for the 1/3 ampacity determination, right?
I'll second Bob's "YES," but I will point out that this situation would require 90C rated terminations. To be explicit, if the termination temperature rating at the tap (i.e., 90C) is equal to or better than (which it would be) the conductor temperature rating (THHN, rated for 90C), then by all means, use the 90C column for the 1/3 ampacity determination.So termination temperature rating at the tap equal or better than conductor temperature rating means, from the perspective of conductor protection, the full ampacity value (e.g. 90?C column value adjusted per 310.15) can be used for the 1/3 ampacity determination, right?
They don't. That is the point that I think you are missing. They don't change the ampacity, they provide a rule that is relevant to the process through which we discover what the ampacity is. As Bob said recently, and as I said earlier, the temperature rating of the terminations is one of the "conditions of use" that comes into play, when determining how many amps a conductor can handle, without exceeding its temperature rating. Other conditions of use include the number of current carrying conductors within a raceway, the ambient temperature, and (for underground ductbanks) the burial depth and soil conditions. You don't know what a conductor's ampacity is, until you take all the conditions of use into consideration.I can see nowhere in the NEC that states 110.14(C) stipulations actually change the ampacity of an insulated wire conductor.
Not correct. What you have is a 225 amp feeder that you tap with a #6 THHN based on the 75? rating of 65 amps, and since your OCP at the end of the tap is rated 60 amps the conductor is adequately protected.... correct? . . . for example you have a 225 amp feeder and you tap with a #6 THHN based on the 90? rating of 75? and your OCP at the end of the tap is rated 60 amps.
Amen Brother...You don't know what a conductor's ampacity is, until you take all the conditions of use into consideration.
So, in your opinion, we can not use the 90? rating to meet the 1/3 ampacity requirement even if we are protected at the 75? rating ?
Seems it would be no different from using the 90? ampacity for derating for conduit fill. The conductor is not overloaded and the insulation is rated for the installation.