KLM
- Orlando, Fl
When applying the adjustment factors for more than three current carrying conductors in a raceway, should the overcurrent protective device trip rating be sized based on the adjusted ampacity? See the example below:
Example: (41) - #10 AWG (90 degree C, THHN) copper conductors are installed in a raceway. Based on Table 310.15(B)(2)(a) an adjustment factor of 0.35 shall be applied. The #10 AWG conductors have an ampacity of 40A based on Table 310.16. Therefore, the adjusted ampacity is 40A x 0.35 = 14A. Article 240.4(B) permits the use of the next highest standard overcurrent protective device. Therefore, a maximum 15A circuit breaker would be required to protect the adjusted conductors.
Are my assumptions correct?