Is it code conpliant to tap the buss right below the main to feed a sub-panel? This is a new GE panel that someone tap the buss to feed the a/c unit. I don't think it is but don't know where to look in the code book.

gus
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
I don't believe the bus bar can be tapped as it is not approved for that. That being said if the tap rules are followed I am not sure it will cause any problems. How was it tapped?
 

guschash

Senior Member
Location
Ohio
Thanks Dennis, They did a nice job on the panel, everything nice and neat. What they did was remove the bolts (2) that connect the main breaker to the buss. They inserted a connector on each buss.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Not a great photo but I have seen lugs attached to the holes in the bus in the background of this photo. That is the bus that is between the main CB and the branch circuit breakers. In that instance I don't really see a problem if all of the tap rules are met.